I have an Art2000 dimmer rack with a weak phase breaker... The breaker for one of the phases in the first module used to be able to carry an 80A load (spread out over channels 1,4,7,and 10 like it's supposed to, but, now, it can't carry a 20A load for very long without popping (also spread out over channels 1,4,7,and 10)
Is this repairable, or do I need to make my employer spring for a new module?
Art2000 Dimmer Rack question
Moderator: Moderators
-
- Posts: 81
- Joined: 05 Oct 2008, 06:24
-
- Posts: 1089
- Joined: 02 Jul 2010, 10:29
- Location: Siegen, Germany
- Contact:
The dimmers are quite modularized. From your description it's not exactly clear which breaker might be affected - the one which can stand 80A is probably the one in the mains distro at the bottom of the rack. You should start swapping modules to find out whether it's a faulty module or a faulty breaker in the mains distro.
It happens rarely, but is not impossible, that a breaker needs to be replaced. I'd strongly recommend to contact your local Avo guru, or seek help from a qualified electrician. Breakers are a safety thing!
It happens rarely, but is not impossible, that a breaker needs to be replaced. I'd strongly recommend to contact your local Avo guru, or seek help from a qualified electrician. Breakers are a safety thing!
-